What is the lowest impedance you have ever seen in a pole or pad transformer? I dont recall seeing anything lower that 1.8%, but I am sure there are lower.
Off the top of my head, 1.7% for sure. When I would be poking around the yard looking at nameplates, the vast majority were 1.7 to 2.1 or so.
15-25 KVA pads and poles I have seen are 1.9-2.3. Impedance seems to go up as the transformer size goes up. This is surprisingly low for a 166. Its a submersible vault unit:
This is an autotransformer @ 1%
Certainly odd for me to see this.
I for sure recall 1.2%. Maybe 1.0x but I would have to look. Don"t ever recall one below 1.0
SCC is 73KA
Freeking mindless. What is the reasoning?
The vault unit I posted in post #3, that was one of a 500 KVA 208y/120 bank, 1.8%. Available fault current is "healthy" to say the least, 77k. Pretty good for a non network service. Service equipment is only 25 feet away, but its well below 65k by the time it gets there.
That 77kA is NOT available fault current. That is the infinite bus fault current. There is a difference and it is important to keep the nomenclature correct.
The available fault current would be based on what the utility is capable of delivering for fault current. This would be then result in an available fault current on the secondary side which is going to less, sometimes substantially so, and will be less than the 77kA.
Correct. I plugged-in some numbers; assumed 1,000 MVA short-circuit power available at primary side, 300 feet of wires--> the available fault current I got was 74kA at the 208V side! I guess it is about that ballpark, IMO.
Yes I know
500kVA pad mount at 1.9%
Two things.
1) That is crazy low for 500. Thanks for sharing that experience because I didn’t know they made them that low for something for that size.
2) We have strangely similar user names. I feel like I have to apologize to you since you joined long before I did. :)