No.Where on the panel schedule you attached does it indicate a neutral is not required?
True, but that has nothing to do with loads on the UP panels. We don't know what they are, at least I don't.You panel schedule shows all 120 volt spare circuit breakers and clearly states 3Ø, 4 Wire which includes a neutral.
True, but that has nothing to do with loads on the UP panels. We don't know what they are, at least I don't.
That is what I thought as well.I thought he was talking about the two 3 pole breakers at the bottom of the panel schedule
I thought he was talking about the two 3 pole breakers at the bottom of the panel schedule
That is what I thought as well.
If you base your answer on the question you thought you were answering I would say you were correct.You guys are correct.
My apologies I read it incorrectly.![]()
If you base your answer on the question you thought you were answering I would say you were correct.![]()
Agree. Going back to my original question - Where does it say a neutral is not, or is for that matter, required for the 100A-3P breakers feeding the other UP panels? The schedule for the panel we can see obviously has one.Yeah, this panel is UP-33A which requires a neutral. Not sure where is says that the other panels 33B and 33C do not require a neutral. It likely would not tell you that on the UP-33A panel schedule.
Agree. Going back to my original question - Where does it say a neutral is not, or is for that matter, required for the 100A-3P breakers feeding the other UP panels? The schedule for the panel we can see obviously has one.
Yes it is a 3P4W panel but why should that have anything thing to do with the load the breaker is feeding in that panel?I'm thinking that it doesn't really matter whether or not there are neutral loads, the schedule clearly says 4W or 4 wire which is what the OP is asking.
I thought he was talking about the two 3 pole breakers at the bottom of the panel schedule
Yes, it should be on the riser diagram.So obviously of panel UP-B&C are 3P4W panels it would require a neutral wire?
....if....So obviously of panel UP-B&C are 3P4W panels it would require a neutral wire?