zcanyonboltz
Senior Member
- Location
- denver
I'm a running an overhead feed to a garage using quadruplex. My question is all conductors are aluminum #4. I have #10 copper left from another job...is it legal to use copper as the grounding conductor in the EMT although all other conductors are aluminum? I know this is not a parallel installation but I am thinking 310.10 (H) requires all conductors to be of the same material. I am using 60A breaker, 250.122 requires #10 copper and #8 aluminum. I am just trying to burn up some copper and am now wondering if my question is legal or not. The new houses I do we run #4 copper ground with 4/0 aluminum from disconnect mounted back to back with panel. I'm looking through 250.120 as I post. Thanks.
Last edited: