Oldmaster2
- PA
- Master Electrician
Been in a debate regarding ground bars and neutral bars. The question becomes, Can you install a ground bar in a main panel and land neutrals on it?
No. You would then be using the enclosure as a circuit conductor. Some might argue that if you put a properly sized wire type jumper from the neutral bar to the EG bar then it would fly. But I think the next argument would be the ground bar is listed only for EGCs.Been in a debate regarding ground bars and neutral bars. The question becomes, Can you install a ground bar in a main panel and land neutrals on it?
I may not be reading this correctly but as you may know, the Neutral/Ground termination bar at a Meter Main panel is one in the same, also it is usually bolted directly to the metal enclosure. Just make sure that the Neutrals should be attached to the same termination bar as the incoming supplied NeutralCan you install a ground bar in a main panel and land neutrals on it?
But if you need more termination points and want to land neutrals on it the new bar can not use the enclosure for neutral current.I may not be reading this correctly but as you may know, the Neutral/Ground termination bar at a Meter Main panel is one in the same, also it is usually bolted directly to the metal enclosure.
200.2(B)Can anyone refer me to the code reference? Thank you
This would be an example of equipment suitable for use only as service equipment.I may not be reading this correctly but as you may know, the Neutral/Ground termination bar at a Meter Main panel is one in the same, also it is usually bolted directly to the metal enclosure. Just make sure that the Neutrals should be attached to the same termination bar as the incoming supplied Neutral