Single Phase Sine Wave
fred-d-c
Tennessee USA
Maintenance Tech
I have a question. Why does the following happen? When you take a scope meter; Fluke 190-204, Putting the Channel 1 test lead on L1 and the ground clip on Neutral you will see the typical -170... +170 volt sine wave at the same time use Channel 2 put the ground clip on L1 and the Channel 2 test probe on Neutral you will see the same sine wave but 180˚ out of phase from Channel 1 measurement.
Same reason that if you take a multimeter and put the red lead on the + terminal of a batter, and the black lead on the - terminal you will get one reading, and when you put the black lead on the + terminal and the red lead on the - terminal you will get the - of that reading.
Voltage (or potential difference) is always measured _between_ two points, and the polarity of that measurement depends on the polarity of the sensor.
With your specific example, you got very lucky, because on most scopes the ground leads of the different channels are common. With most scopes if you try to repeat the experiment you will measure the available short circuit current of your 120V supply, and likely the fecal containment capacity of your pants.
-Jon
-Jon
Yes I was aware not to attempt that with a typical scope. Does that mean that the Neutral is alternating too?
(oh no, not this again)
... Does that mean that the Neutral is alternating too?
That question has no real meaning. As Jon said a voltage (alternating or not) is always between two points. Therefore a single point cannot 'alternate.'
(Also, technically you don't have a neutral unless you also have an L2, which you've not mentioned yet.)
If you connect a DC volt meter to a battery, red to positive and black to negative you see the voltage displayed. If you swap the leads, black to positive and red to negative you see the voltage displayed but with a (-) sign in front of it.
If you can understand why that happens you should have no trouble understanding your waveforms with swapped leads.
-Hal
As I noted, voltage can only be measured between two points. It is impossible to say that one point or the other is alternating, only the voltage between them.
However: it is very common to pick a reference point and _define_ it as being a fixed '0V', and then the voltage difference between this reference and any other point can be associated with those points. Generally 'ground' is _defined_ as 0V, and since the neutral gets 'grounded' then in this scheme the neutral is also at a fixed '0V'. But this is a definition, not physics.
-Jon
I believe most people use the term neutral interchangeably with the grounded conductor. Some even call it the white wire....LOL
I wouldn't always bring it up just to nitpick, but in this case it has some relevance to the subject, since a neutral is defined by the vector sum of waveforms.
I understand a lot what everyone is saying, and thanks for all the responses, I have learned some things. I do understand why swapping the leads from + to - causes the meter to go from + to -. I am still not sure I totally get why it is 180˚ out of phase, if I keep thinking about it surely I will have an aha moment. Keep in mind, I am not an electrician and certainly not an EE or Physicist. I do tinker with things both mechanical and electrical and have for years. when I run into something I don't fully understand, I start digging in.
Danger Will Robins!
You have walked into one of the never ending discussion triggers. Lots of different folk have very strong opinions on the topic.
When you swap the leads you invert the measurement. An inverted sine wave looks _exactly_ like the same sine wave offset by 180 degrees, and in situations that require phase offset (like the stator of a 3 phase motor) an inverted sine wave can be _used_ like a sine wave offset by 180 degrees.
Weather it is actually a 180 degree phase offset or 'merely' an inversion is a philosophical discussion that will stretch for north of 1000 posts :)
-Jon
This is an issue that always causes problems with discussion of whether or not 120-0-120 is single phase or two phase.
The 180 degree phase shift is different from all other phase shifts when looking at a sine wave:
A 180 degree phase shift is exactly the same as reversing the polarity of the sine wave.
(A trigonometric identity tells us that sine(180+theta) == -sine(theta) )
We had quite the debate about this a few years ago. We concluded that it is a polarity issue that, because it involves AC, merely resembles a 180-degree phase shift. If it involved DC, there would have been no polarity-vs-shift debate.