mbrooke
Batteries Included
- United States
- Technician
All right- correct me if I'm wrong... The graphic has 583 amps... This means a 100 amp breaker will take 3 seconds (average) (6 seconds max) to clear the fault according to these time current curves:
https://library.industrialsolutions.abb.com/publibrary/checkout/GES-6203B?TNR=Time Current Curves|GES-6203B|PDF&filename=GES-6203B.pdf
Assuming a 40/60 voltage drop to the concrete someone is standing on this would provide about 72 volts potential assuming an infinite source.
Now, 72 volts on a 100 ohm hand to feet value:
Means 720 milliamps of current will pass through the body during those 3-6 seconds of clearing.
This would put us in the AC-4 region of the body graph:
OK, so... It looks like I'm missing something
I'm lost guys.
Source impedance to high? Wire impedance not right? Hmmm...