Good question. The answer lies in Note 2 to the table, which tells you that Effective Z is just R cos(theta) + X sin(theta), where theta is the power factor angle, i.e. tan(theta) = 0.85. It further notes that this value is for calculating voltage drop.How can Effective Z at 0.85 PF for Uncoated Copper Wires be of a lower impedance value than Alternating-Current Resistance for Uncoated Copper Wires?
The short answer is that for calculating the magnitude of fault current, where there is no load impedance in the circuit, you can ignore the Effective Z column. You just want the total impedance |Z| = sqrt(R^2 + X^2) for Ohm's Law.
The long answer is a bit more complicated and I'm not sure I have all the details squared away. But the basic idea is that if you are just interested in calculating voltage drop on the supply wiring, then for a load with a non-unity power factor, the reactance of the supply wiring may "cancel" some of the reactance of the load and give you less voltage drop on the supply wiring than you would have for a purely resistive load. I think.
Cheers, Wayne