What should be the grounding procedure for Wye-Grounded Primary and Wye Grounded Secondary TRANSFORMER to be considered as Separately Derived System?
Is it considered SEPARATELY DERIVED SYSTEM if they have Common GES? What is GES?The H0 and X0 are common (they can be isolated if need be) so they both connect to the GES and from there all bonding is as normal.
Roger
Grounding Electrode SystemWhat is GES?
Maybe, I think it depends on what voltages we are talking about and why this particular transformer is being used and what for. IF the primary is an MV MGN, primary neutral would be grounded.Bobby, just so it gets mentioned, the primary's neutral should be left floating, not grounded or "neutral'ed", as if it was a delta.
I dont think that is the case. Most utility pads are Wye-Wye and always have the primary neutral grounded.My understanding is that three wye-connected individual transformers can have the primary neutral grounded, but a single, three-phase unit can not.
One 3ph or three 1ph?The building I'm working in now has wye wye 4160-2400/208-120 transformers.
Larry I think it's wye-delta that is an issue with common core but not if made from three individuals.One 3ph or three 1ph?
Sounds familiar. Thanx!Larry I think it's wye-delta that is an issue with common core but not if made from three individuals.
I've been reminded that the issue is with single-unit 3ph wye/delta transformers.Three phase.
Please elaborate. I don't want to thread jack but I don't think I am.I have usually said; do not ground the primary side of wye-wye transformers unless you are a utility.
The reasoning behind this statement is that most industrial/commercial electricians would be involved with <600V on the primary side while utilizes would be using medium voltage primaries. I kind of skipped the situations where a facility use MV as its distribution system, like the OP has.
To answer the OP, the primary side neutral point being connected to ground/earth/building steel is not related to the secondary neutral point being connected to the same reference points.
I am curious too. There is that often cited paper "the whys of the wyes", but it is quite technical in nature, Ive never been able to slog thru it without my brain hurting.Please elaborate. I don't want to thread jack but I don't think I am.
I understand ferroresance is typically only a concern with MV primaries, but I dont see why the other potential issues are only a concern at MV voltages.