Special thanks to Tom and Dale.
I feel confident about allowing this installation to proceed.
Kwired: wouldn’t the 24VDC Input/Output act as the relay you’ve noted?
Unless the individual i/o outputs are tested and listed as Class 2 power sources, the fact that the power supply to the PLC is Class 1 governs the entire installation. A dry contact output which is used with a separate Class 2 supply might qualify as the necessary isolation.
The basic question is not whether the PLC outputs are Class 2 or not. If you want to run wires attached to those outputs in a circuit reclassified as Class 1 so you can combine the wires with power wiring in the same conduit, then whatever the output is driving must NOT be limited to use in a Class 2 circuit.
If you reclassify input wiring to the PLC as Class 1, then the PLC must not rely on the inputs being Class 2 or dry contacts for safety.
Sent from my iPhone using Tapatalk