Type MC cable
mbrooke
Batteries Included
United States
Technician
Why doesn't type MC cable have a bonding strip? What if the middle of the run was damaged or drilled into?
Because it has an insulated green conductor as the EGC. The jacket is still bonded by the connector at each end and not designed to carry the circuit fault current but I see your point if the jacket itself was faulted by a screw or something.
Without the bond strip the jacket would present a high impedance path during a fault internal to the cable itself.
My guess is that the odds of it being a problem are very slim so it's not a concern.
It should be bonded on both ends if properly terminated.
So if damaged in the middle, it would have a fault part either way.
Smart MC cable has a bond strip if that is a concern, then switch to it. It saves 30% time on installations.
Write a proposal for a ban due to the infinitesimal possibility that something bad can happen. Infinitesimal with no substantiation seems to dictate what they'll approve. :rolleyes:
I will bet if the MC cable is so damaged the the EGC is severed, a bonding strip will not be much better.
The outer shell of armored cable is 5-6X's the conductors inside, thus significant Z dif. In older homes typical with horsehair plaster ,it was not uncommon to find a line of dots , not necessarily rust , from it ~RJ~