Wanna see that. Betcha it had nothing to do with the lack of a bonding strip.
-Hal
I'd upload the PDF but the forum won't let me:
Wanna see that. Betcha it had nothing to do with the lack of a bonding strip.
-Hal
Bonding is a big issue in Hazardous Locations since circulating currents could cause a spark. (I know it isn't supposed to happen with proper bonding but hazardous locations often take a "belt and suspenders" approach. {Section 501.30(A)] All three construction types are fine in Class I. Division 2 [Section 501.10(B)(1)(5)] when installed per {Section 501.30(A)]. They would be fine in Division 1 also except interlocked armor has the potential for transmitting gases,METAL-CLAD CABLE (PJAZ)
GENERAL
This category covers Type MC metal-clad cable. The cable is rated for use
up to 2000 V, and certified in sizes 18 AWG through 2000 kcmil for copper,
12 AWG through 2000 kcmil for aluminum or copper-clad aluminum, and
employs thermoset or thermoplastic insulated conductors. It is intended for
installation in accordance with Article 330 of ANSI/NFPA 70, ‘‘National
Electrical Code’’ (NEC).
The cable consists of one or more insulated circuit conductors, a grounding
path (grounding conductor, metal sheath, or combination thereof) as
described below, one or more optional optical fiber members, and an overall
metal sheath. The metal sheath is an interlocked metal tape, a corrugated
metal tube, or a smooth metal tube. The metal sheath of single-conductor
cable is nonferrous. A nonmetallic jacket may be provided under and/or
over the metal sheath. Cable with metal armor, rated 2400 to 35,000 V is
covered under Medium-voltage Power Cable (PITY) and is marked ‘‘Type
MV or MC.’’
Cable with interlocked armor that has been determined to be suitable for
use as a grounding means has interlocked aluminum or steel armor in
direct contact with a single, full-sized, bare aluminum grounding/bonding
conductor. This cable is marked to indicate that the armor/grounding conductor
combination is suitable for ground. The equipment grounding conductor
required within all other cable with interlocked armor may be insulated
or bare, may be sectioned, and is located in the cable core but not in
contact with the armor. Any additional grounding conductors of either
design have green insulation. One insulated grounding conductor may be
unmarked, one other may have only a yellow stripe and the balance have
surface markings that indicate they are additional equipment grounding
conductors or isolated grounding conductors.
The sheath of the smooth or corrugated tube Type MC cable or a combination
of the sheath and a supplemental bare or unstriped green insulated
conductor is suitable for use as the ground path required for equipment
grounding. The supplemental grounding conductor may be sectioned. When
sectioned, all sections are identical. Each additional green insulated grounding
conductor has either a yellow stripe or a surface marking or both to
indicate that it is an additional equipment or isolated grounding conductor.
Additional grounding conductors, however marked, are not smaller than
the required grounding conductor.
I don't believe that this failure mode warrants a change in the requirements for MC cable.
So your good with a panel full of GFCIs?
Write a proposal for a ban due to the infinitesimal possibility that something bad can happen. Infinitesimal with no substantiation seems to dictate what they'll approve.
But I guess the inner wrap doesn't have to be dielectric in the paper can be used:
9:40 shows paper insulation with the bond strip, but not on normal MC.
I want to say manufacturers are "double insulating" MC when it doesn't have a bonding strip.
Possibly, but:Hmmm... basically lots of options... But I take it manufacturers choose "A nonmetallic jacket may be provided under and/or
over the metal sheath" when the armor is without bond strip?
If the paper were to interfere with the ground path, UL wouldn't permit marking it or list it under their Standard. Use any other way would violate Section 110.3(B).Cable with interlocked armor that has been determined to be suitable for
use as a grounding means has interlocked aluminum or steel armor in
direct contact with a single, full-sized, bare aluminum grounding/bonding
conductor. This cable is marked to indicate that the armor/grounding conductor
combination is suitable for ground.
Possibly, but:
If the paper were to interfere with the ground path, UL wouldn't mark or list it under their Standard. Use any other way would violate Section 110.3(B).
This UL 1569 may hold the answer to that .......~RJ~
And what theory is that?In no disagreement. But thats really throwing electrical theory underneath the bus.
And what theory is that?
And how did it get "thrown under the bus" assuming it was otherwise installed correctly?
[/QBTW that's not "electrical theory" like a Maxwell equation; it's simply a Code requirement. Sections 250.4(A)(3), (4), & (5) are the easiest to cite. There are requirements for specific types of installations throughout Article 250 and the rest of the Code. (There's nothing theoretical about it
What if the middle of the run was damaged or drilled into?
In that case, you are a perfect example of last sentence of Section 90.1(A) and have been for a long time.Faults can and do happen. Nothing stops a nail through MC or damage during termination.
...
And thats the precisely the issue at hand. Effective ground fault current path is not defined. Ohms law is thrown under the bus.
Also, MC "smart cable"? What's the difference between that and type AC?? For me, the advantage of MC is the integral EGC that provided a reliable ground, unlike AC that relied on the integrity of the connectors. So now, in the name of cutting labor costs they are back pushing what is actually AC cable and again relying on the connectors? I ain't buying it!! If they want to reinvent AC fine, but don't call it something it isn't and say how great it is just to sell product.