@ 25 ohms is the resistance to the ground, but, if the transformer is far injecting a current in the electrode won't be 4 Amps it would be less because at distance the earth potential is different.a normal breaker will not trip if the hot wire is tied to an electrode as an electrode @ 25 ohms would generate an approx 4 amp load. the Nuetral/grounded conductor that returns back to transformer is where the fault will trip. We do connect the EGC to the GC at 1 point only. I stand corrected as my comments did refer to the electrode system's purpose.