Derating in A nipple.

Status
Not open for further replies.
yes (as far as derating for number of conductors..310.15(B)(3)}
 
There shouldn't be anything else that can factor in to make the chart void ?

Just covering all bases, the 24" "exception" is under conductor, it would be rare but ambient adjustment would still apply I believe.
 
Just covering all bases, the 24" "exception" is under conductor, it would be rare but ambient adjustment would still apply I believe.
Agree, ambient temp adjustments still would apply.

Keep in mind the exception to 310.15(A)(2) could possibly come into play in some situations and you may not need to make the adjustment.
 
Status
Not open for further replies.
Top