Is it true that in a nipple of 2 feet or less that derating does not apply and that only wire fill would apply to that nipple ?
Thank you.yes (as far as derating for number of conductors..310.15(B)(3)}
There shouldn't be anything else that can factor in to make the chart void ?yes (as far as derating for number of conductors..310.15(B)(3)}
And wire fill can be up to 60% per Chapter 9 Notes to Tables(4).Is it true that in a nipple of 2 feet or less that derating does not apply and that only wire fill would apply to that nipple ?
There shouldn't be anything else that can factor in to make the chart void ?
Agree, ambient temp adjustments still would apply.Just covering all bases, the 24" "exception" is under conductor, it would be rare but ambient adjustment would still apply I believe.