240V 1000W HPS lights are a pain. Unfortunately you cant connect 4 on a 20A circuit because they are around 4.4A each (277 works good for these as you get 4 per 20). So you are looking at 3 per two pole 20 breaker. How exactly were you proposing to connect them to a three pole breaker?I have 240 volt 1000 watt HPS lights. Is there a problem connecting six of these to a 3P20 breaker? I have a 240V delta 3-phase system.
That's easy: 2 on A-B, 2 on B-C, and 2 on C-A.How exactly were you proposing to connect them to a three pole breaker?
I’ve done similar in the past. Seemed to work fine at the time.That's easy: 2 on A-B, 2 on B-C, and 2 on C-A.
Yes that would certainly work. 2 -2 pole breakers would be a lot cheaper, but I just realized the OP said delta system so he would need straight rated 2 poles which I would guess have a big price jump so maybe using a 3 pole makes sense.That's easy: 2 on A-B, 2 on B-C, and 2 on C-A.
Am I missing something, he wants to connect 6 luminaires, if they do draw 4.4 A each then you would put two between each phase and have 8.8 amps. That x 1.732 because of what is between the other two phases gives you 15.24 amps on each of all three phase conductors.240V 1000W HPS lights are a pain. Unfortunately you cant connect 4 on a 20A circuit because they are around 4.4A each (277 works good for these as you get 4 per 20). So you are looking at 3 per two pole 20 breaker. How exactly were you proposing to connect them to a three pole breaker?