120/240V panel fed from a 208/120 source.
Ozymandias
Missouri
Hi all,
I have a job where I have a 200A fused disconnect with two phases(208/120), the neutral and ground. I will be running feeders a 120' away to a panel which will feed rows of refrigerators.
Is it permissible to use two phases out of the three?
I assume so since that disco fed a panel which is no longer there, and because only two phases are available could I use a 240/120V panel.?
A three phase panel would only have two buses energized. On the 240/120V panel, only 120V circuits would be used from the panel, I understand I would only have 208V available instead of the usual 240V. Thanks for the input!
Hi all,
Two phases of a three phase system is single phase, you can use a regular single phase 120/240 panelboard, absolutely. Done all the time.
Hi all,
Delta or Wye
I beleive that all 120/240 volt panels are listed for use on a single phase 208/120 wye system. As electro stated it's done all of the time especially in apartment building construction.
If it is a 208/120 source, then it is wye or the equivalent. (In theory it could be a 208V delta plus a grounding transformer but this would be the equivalent of a common wye source.)
If the source were delta, then it would be 240V with 120/240V available by taking the two legs from the center tap coil, and the third leg (the stinger) would be 208V to ground.
Jon
Delta or Wye
Jon
Yes, I was concerned about it because it’s such an old building, but once I measured 208/120V at disconnect I am assuming it’s a WYE,😬.
I would never install a 200 amp single phase sub panel due to it could overload 2 of the existing 3 phases. It would be best to install a 120/208 3 phase panel. would not cost that much more for the additional line conductor and a 3 phase panel. Best practice is to look at future needs. we never ran any motor over 2 HP on single phase. If you do place a large load on only 2 of the 3 phases you run the risk of voltage drop on the 2 phase that will cause 3 phase motors to run hotter then normal. Too many customers want the cheapest job but if it was me I would walk away from a job where they insisted on a single phase 200 sub panel. Work safe & STAY HEALTHY.
e
e
Interesting. That’s what made me pose the question, that I could unbalance the loads. The main disco is 400A and each leg under load hovers around 60A. Downstream a 200A fused disco(two legs/phases/208V) feeding the 200A 40 space panelboard that will power 80 refrigerators continuously.
The apartment building situation is much better balanced since roughly 1/3 of the apartments use each pair from the three possible pairs.
A single large and unique unbalanced load is troublesome.
Sent from my Pixel 4a using Tapatalk
Am I thinking correctly here?
If I have 80 refrigerators at 5 amps average for a total of 400 amps, divided by 3 phases to equal 133 amps per phase?
I’m trying to size the panel board,
Thank you all for the help.
You should balance the number of refrigerators then calculate your amps.
80/3 = 27 on the highest loaded leg. 27 x 5 = 135A for the largest conductor/phase.
I would definitely go with 3ph and use 4-wire MWBCs.
I agree. I did not catch how many circuits would be needed in the OP. OP remember you will need three pole breakers. Technically you can use single poles with a 3x handle tie, and it will be less than half the cost of a three pole however note not everyone makes a three pole handle tie. Siemens does not. They are available for Eaton BR.
Thanks for the tip, but are you referring to a main breaker at the panelboard or just the individual breakers feeding branch circuits.
I think in the end I’ll have a 3 phase
disco(fused or with a breaker) and travel about a 100’ to the 3 phase panelboard which will either be an MLO or a 3 pole main breaker panel with individual single pole breakers feeding branch circuits.
Sorry for the confusion Electrofelon.