Jerramundi
- Chicago
- Licensed Residential Electrician
It is if utilization equipment is supplied.A juction box is not a outlet. Read the Article 100 definition.
Generally speaking, to discern the NEC definition of an "outlet" from the common vernacular which confuses it with a receptacle, we typically refer to "outlets" as "any point in which the circuit wiring is accessible." Technically speaking, you are correct that per the NEC definition, it requires utilization to meet this definition and a junction box simply used as a pull point would not qualify. However, given the accessibility of the wiring at pull point junction boxes, any junction box could theoretically become an "outlet" in the future. I still refer to all junction boxes as outlets and see no reason to change that.
Since you obviously want to flex technical speak, I will do the same. It's not that metal wiring methods do not require protection. It's that metal wiring methods between the panel and the first opening do no require protection IF protection is provided at the first opening... I'm just being technicalIf wiring protected by metal wiring methods does not have to be protected, then why do I need protection at the outlet the if the circuit never extends beyond such wiring methods? The protection requirement makes some sense if the device is a receptacle, or a light fixture with exposed live parts in the socket when a bulb is removed (or into which someone can screw an old fashioned ungrounded receptacle). It doesn't make any sense if the device at the final box is the end use of the circuit. It seems like they didn't think of this.
It does make sense if the device at the final box is the end use of the circuit because you're going to plug in utilization equipment with conductors and the goal is protect those conductors from arcs.
I do agree that this exception (i.e. at the first opening) is a bit odd. It stands to reason that if protection is required on the entire circuit downstream of the first opening, that the entire circuit should be protected.
IMO, it seems like something that was added to aid in the transition to AFCI requirements because if there is an existing MWBC you can separate it at the first opening and AFCI protect one or both circuits. It also aids in the transition because potential compatibility issues with AFCI breakers and panel types. I would wager it will eventually go away as we phase further and further into expanded AFCI requirements.