I'm surprised you don't see all 30s.Is it just me or do I see 15, 20s and what I think is one 30A fuse on wire that’s all the same size?
Anything is doable, how much money is the question. And getting that panel junked is going to be a lot of trouble if it’s done right with the abatement & containment costs.
It can done. Hope you have a lot of money for the EC.
The 30 is for the A/C starting current.Is it just me or do I see 15, 20s and what I think is one 30A fuse on wire that’s all the same size?
Have you seen AFCI that work on more than 3-wire circuits?Complete Rewire is the best solution. I understand there are AFCI available that will supposedly work with common neutrals. I have not used them and do not know the brand name.
Will they actually work on N&T? IDK.
I've had that happen numerous times. They've painted and finished the walls then call the electrician . Ask them if they have saved any matching paint?homeowner has been finishing areas and painting. i hate telling them the bad news. I've only seen 3-wire afci breakers. I interested to hear if anyone has an afci solution?
What about 210.12 (A) ? I'm curious...You may be better off with AFCI receps.
Well my first thought is that AFCI breakers are not required for this panel change out. however OP mentioned changing out receptacles which would evoke the fascist and atrocious afci requirement in article 406. It seems that was revised a bit for 2017 but it doesn't look like any of the exceptions would apply.What about 210.12 (A) ? I'm curious...
Not a fan of GE panels and breakers, but their AFCI's don't have a GFP component and would work with common neutrals.Don’t care about asbestos, has nothing to do with NEC. Been swimming in nasty attics since 1997. The common neutral is where I am having a problem. If money isn’t an object what’s the best way you guys see?
The goal is to get breakers and grounded receps in a few locations. Can NM still be tied into k&t with afci protection?
Yeah, I wouldn't touch that without a complete rewire. I wouldn't want to live there. Does the customer think that AFCIs are a solution for not replacing that old wiring?Complete Rewire is the best solution. I understand there are AFCI available that will supposedly work with common neutrals. I have not used them and do not know the brand name.
Where are the neutrals for the branch circuits?Can this be changed out so that afi/gfi breakers could be installed? Customer wants 3wire receps and
nice work to the old timers. Hopefully they had a Covid mask to protect from the asbestos lined panel
They are right there. Next to their fuses.Where are the neutrals for the branch circuits?