I agree! This particular project was originally pulled under a state permit. Do to reason too long to explain the county decided to take over inspections in this area. When they did that the we had to pull a final permit through the county in the 2020 cycle. I haven't pushed too hard yet. The project owner is a little nervous of me ruffling the feathers until necessary.Generally, the code in effect when the permit is pulled is what gets enforced. It can be hard to hit a moving target.
Is 210.8F referring to all outlets or just receptacle outlets? I’m not on 2020.
Hmm I don't know but I'll checkDon't the installation instructions for a GFCI limit the number of feet past the GFCI?
I thought I ran into this years ago
You might be on to something. It appears through an old MH post more than 150'-200' will cause tripping.Don't the installation instructions for a GFCI limit the number of feet past the GFCI?
I thought I ran into this years ago
there you have it!!Square D 2 pole GFCI:
"Do not connect circuit breaker to
more than 250 ft. (76 m) of load
conductor for the total one-way run."
Then politely ask your inspector to quote the article you are violating.Thank you all for input on this.
It is hard wired.
The yellow wire is not the EG. It is a motor lead.Seems to me if the yellow wire is used as EGC (which many times it is unless it is connected to a start controller) your readings from leg to this yellow (ground) should not be 3-11 ohms. You have a ground fault!
It could be, if the pump has been installed for several years that if the wire leading down to the pump has not been taped often to the down pipe it can get lodged and rubbed against the well casing every time the pump kicks in wears at it.
article 210.8F there is a jbox on the top of the well head.Then politely ask your inspector to quote the article you are violating.
The well pump conductors are #10AWG and that is the majority of the run.
210.8(F) GFCI Protection. Outdoor Outlets.
An “Outlet”, according to the NEC Article 100 definition, is a point on the wiring system at which current is taken to supply utilization equipment.www.electricallicenserenewal.com
IMHO this is an excessive requirement for underground wiring to a submersible pump (unless that pump is in a body of water where people swim), but it appears to be required under 2020 code.
I amend my last post to 'if the leakage were reasonable given such things as expected leakage from capacitive coupling, then I would request a waiver from the AHJ to use GFPE rather than GFCI'.
-Jon
Hmm I don't know but I'll check
Then politely ask your inspector to quote the article you are violating.
article 210.8F there is a jbox on the top of the well head.
I agree that the "outlet" is not outdoors in this situation.I think this also raises a question of "outlet" definition as it applies to the typical submersible pump in a well in a residential setting. In most cases the "outlet" is within the structure and the branch circuit extends from that "outlet" directly to the well head. In other words the outlet is not outdoors as the first word of 210.8(F) says.
This post serves as a good example of how out of touch the CMPs are with the real world. They have gotten into the habit of requiring things that either are not yet available or not reliable. I don't see how you could expect a class A GFCI to work in this situation or for the submersible manufacturer to support this.
I think this also raises a question of "outlet" definition as it applies to the typical submersible pump in a well in a residential setting. In most cases the "outlet" is within the structure and the branch circuit extends from that "outlet" directly to the well head. In other words the outlet is not outdoors as the first word of 210.8(F) says.