romex jockey
- Vermont
- electrician
would this w/a contactor >>>>
meet 210/8(B)
~RJ~
meet 210/8(B)
~RJ~
The specs don't tell us if it is Class A. Guessing that since it is not UL listed and only Recognized we are SOL.
would 'trip point' qualify>>>?The specs don't tell us if it is Class A. Guessing that since it is not UL listed and only Recognized we are SOL.
| Trip Point | 5, 10, or 30 mA selectable |
Something along the lines of this with the right breaker and enclosure type, NEMA 1 or 3
Roger
Steve you would simply purchase the appropriate GFCI breaker and install it in the enclosure.thx Rog, but i'm looking to meet code re> 210.8
the bummer is the market appears to be less than accommodating
~RJ~
I would if they made one Roger,Steve you would simply purchase the appropriate GFCI breaker and install it in the enclosure.
Roger
The supply panel wouldn't matter Steve. You can mount another manufacturers disconnect (enclosed breaker) downstream.I would if they made one Roger,fwiw....the panel is a 3ph GE
~RJ~
another manufacturers 3 phase gfci breaker ?The supply panel wouldn't matter Steve. You can mount another manufacturers disconnect (enclosed breaker) downstream.
Roger
My question is similar. Who makes them?another manufacturers 3 phase gfci breaker ?
~RJ~
That one you posted is also QOB - not sure if there is single breaker enclosures for QOB breakers or not, but they also do have plug on types in two and three pole GFCI's in catalog, not necessarily for every standard overcurrent device size. Not certain how readily available they are either. Price - probably don't want to know.If I understand roger's suggestion correctly, he is suggesting that you mount something like this:
in a small 'stand alone' panel that only contains the one breakerQOB320GFI - Mini circuit breaker, QO, 20A, 3 pole, 208Y/120VAC, 10kA, 6mA grd fault A, pigtail, bolt on mount | Schneider Electric USA
Schneider Electric USA. QOB320GFI - Mini circuit breaker, QO, 20A, 3 pole, 208Y/120VAC, 10kA, 6mA grd fault A, pigtail, bolt on mount.www.se.com
and run a feeder from your supply panel to this small stand alone panel
But arrrrrgh on the price....
-Jon