Something along the lines of this with the right breaker and enclosure type, NEMA 1 or 3

1621776041919.png

Roger
 
If I understand roger's suggestion correctly, he is suggesting that you mount something like this:
in a small 'stand alone' panel that only contains the one breaker

and run a feeder from your supply panel to this small stand alone panel

But arrrrrgh on the price....

-Jon
 
Jon has it. Don't pay a lot of attention to prices on SQ D's website however it would still be expensive I'm sure.

Roger
 
If I understand roger's suggestion correctly, he is suggesting that you mount something like this:
in a small 'stand alone' panel that only contains the one breaker

and run a feeder from your supply panel to this small stand alone panel

But arrrrrgh on the price....

-Jon
That one you posted is also QOB - not sure if there is single breaker enclosures for QOB breakers or not, but they also do have plug on types in two and three pole GFCI's in catalog, not necessarily for every standard overcurrent device size. Not certain how readily available they are either. Price - probably don't want to know.
 