texie
- Fort Collins, Colorado
- Electrician, Contractor, Inspector
I didn't say I had an opinion on this. I was just citing facts.An older rule makes it less likely to be relevant today IMO.
Neither of those apply code is code. You could mess up with something energized just as easy as de-energized. Sound but hurt I failed an inspection imopIn that case code would not allow MWBC, and OSHA would be ok with live work.
I didn't say I had an opinion on this. I was just citing facts.![]()
to sell barriers.....~RJ~Any idea on the code's reasoning?
Safety for anyone working on or replacing switches?Any idea on the code's reasoning?
But I'm reluctant to circuit any interior lights at 277V anymore. With lower power draws of LED, there isn't that much advantage to using 277V.
And with grounded ceiling grids, working on 277V lights is one of the most likely places for someone to get hurt. Combine that with the qualifications and training for a typical "maintenance person".....
Doesn’t it have to do with the manufacture voltage rating of the switches themselves perhaps? If you have a 120v switch that’s max rating is 300...? The. To put it in an enclosure exceeding that would violate the installation and pose a fire hazard?...
In that drawing that Smart$ posted, both "systems" are wye systems and both neutral points are bonded together.Awesome!
But I want ask- where does the 30 degree phase shift come from? I'm guessing from a delta-wye transformer? In that case how is the circuit path completed? Would the transfomer's vector group make a difference?
I don't know exactly how to draw it out but guessing if you had a corner ground delta on either side that grounded corner needs to be at same point as the neutral of the wye when you draw it out. That should result in different dimensions from ends of each primary to each secondary line than the wye-wye ended up with. Change the delta to high leg delta and you move things around again.