404.8 (b)

Status
Not open for further replies.

Clayton79

Member
Location
illinois
Occupation
Owner/operator
Doesn’t it have to do with the manufacture voltage rating of the switches themselves perhaps? If you have a 120v switch that’s max rating is 300...? The. To put it in an enclosure exceeding that would violate the installation and pose a fire hazard?...


Sent from my iPhone using Tapatalk
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Any idea on the code's reasoning?
Safety for anyone working on or replacing switches?

But I'm reluctant to circuit any interior lights at 277V anymore. With lower power draws of LED, there isn't that much advantage to using 277V.

And with grounded ceiling grids, working on 277V lights is one of the most likely places for someone to get hurt. Combine that with the qualifications and training for a typical "maintenance person".....
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Safety for anyone working on or replacing switches?

But I'm reluctant to circuit any interior lights at 277V anymore. With lower power draws of LED, there isn't that much advantage to using 277V.

And with grounded ceiling grids, working on 277V lights is one of the most likely places for someone to get hurt. Combine that with the qualifications and training for a typical "maintenance person".....


You saying line to line 208-240 is good? 😃
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Doesn’t it have to do with the manufacture voltage rating of the switches themselves perhaps? If you have a 120v switch that’s max rating is 300...? The. To put it in an enclosure exceeding that would violate the installation and pose a fire hazard?...


Sent from my iPhone using Tapatalk


How though? Both yokes are grounded, and there is ample air space between the devices such that dielectric breakdown will not occur steady state or reasonable voltage swells imo.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Awesome!

But I want ask- where does the 30 degree phase shift come from? I'm guessing from a delta-wye transformer? In that case how is the circuit path completed? Would the transfomer's vector group make a difference?
In that drawing that Smart$ posted, both "systems" are wye systems and both neutral points are bonded together.

I don't know exactly how to draw it out but guessing if you had a corner ground delta on either side that grounded corner needs to be at same point as the neutral of the wye when you draw it out. That should result in different dimensions from ends of each primary to each secondary line than the wye-wye ended up with. Change the delta to high leg delta and you move things around again.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
In that drawing that Smart$ posted, both "systems" are wye systems and both neutral points are bonded together.

I don't know exactly how to draw it out but guessing if you had a corner ground delta on either side that grounded corner needs to be at same point as the neutral of the wye when you draw it out. That should result in different dimensions from ends of each primary to each secondary line than the wye-wye ended up with. Change the delta to high leg delta and you move things around again.

o_O

I'm picturing a wye supply going into a Dyn01 step down.
 