electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
I live in a rural area and due to high utility installation costs to extend primary, I frequently run into situations where taking service at 240 and stepping up to MV and then back down is the only option (typically this becomes cost-effective around 1500 ft). 240 is the only service voltage available to a dwelling, they will not provide MV and they will not provide 480 or 600 or anything else just in case anybody asks.
So I do these occasionally, and I'm always a bit torn on the transformer size. 25kva seems to be sort of the standard, just because the one other guy in the area that does this uses that size, and that is the size the utility provides service with for a typical residential project.
The big concern in my mind is no load losses, since the customer is of course paying for them, so there is an incentive to keep the transformers as small as possible. 2010DOE pad mounts, based on measurements I have taken, have a no load loss of around .25%, DOE2016 a little less. So this is about $85 per year for two 15KVA and $145 per year for two 25KVA.
Capital cost of course comes into play with a 15 KVA being theoretically cheaper, but these things are usually acquired on eBay or the surplus/refurbished market so it's a crap shoot as to availability, so let's just ignore the capital cost.
On the other hand, it seems there is better power quality with larger transformers, less voltage sag under load. For example a 25 KVA at full load will have more voltage drop than a 50 KVA at half load. So this is the part I struggle with: weighing The increased losses versus The increased voltage stability and voltage regulation, which is not insignificant now that you have three total transformers basically in series before it gets to the house.
So what size would you choose? What about if it was your house? What about if it for was for a client would you have a different answer? And to preempt what seems to be the glaring missing piece of information, what the load is.......this is in the Northeast, where there isn't really much air conditioning maybe a window unit or a small mini split. It's cold enough that nobody really uses significant electric heat other than maybe 2,3, or 4 KW total, electric dryer, electric range maybe, nothing like on demand electric water heaters, just a 4500 watt tank, maybe a hobby workshop with a 3 horsepower table saw tops. Basically your kind of typical place where my rule of thumb would be the load will only ever get to about 60 amps and even that would only be quite brief. Don't consider NEC load calcs. Okay have at it.......