- Illinois
- retired electrician
How is this product that uses a cord to extend power from one outlet to another not a 400.12(A) violation?
I skipped right over that. ThanksBecause it is explicitly allowed by (2017) 400.10(A)(11)?
Cheers, Wayne
Don referenced 400.12(A), but presumably meant 400.12(1) (assuming 2017), which is "As a substitute for the fixed wiring of a structure". As you point out, the in wall portion of the product is a Chapter 3 method, so that was not the concern.It's not what you think. 400.10(A)(11) still does not allow flexible cordage to be run within the wall.
So question, if the existing system did not have AFCI requirement at time of installation, will this extension of wiring be exempt from 210.12 as it is essentially an extension cord?