A/A Fuel GTX
- WI & AZ
- Electrician
At what height is the PVC pipe?Does this violate 110.26? It's in a basement and the white PVC is the main drain for the plumbing system.
The PVC is roughly 7' off the floor. This is a basement with an 8' ceiling. I'm installing a new service at this house. The PVC looks relatively new so the plumber caused this situation. The location of the PVC doesn't pose a problem to me but I don't want to get tagged upon inspection. It's darn near impossible to adhere to all 110.26 requirements in most basements.At what height is the PVC pipe?
Is it hurting anybody? Is it ever likely to get in the way of somebody working on the equipment? Since the answer to both of these questions is no, what is the purpose of the rule in this case other than an arbitrary rule that just gives inspector something to nitpick about.
That would seem to be a design choice, and not a safety issue.Also if the pipe starts to leak do you really want that over the panel...
What is inherently unsafe about it? It's no more unsafe than if you had a pressurized water line a few feet away out of the working space that might develop A leak and spray all over the panel.Have you read the code lately? Much of it is a design issue but imo this is a bit of a safety issue
NEMA 3 enclosures? If not it is a safety issue. Sewage leaking onto and into the enclosure not good. Also I went into electrical because didn't want to deal with other people sewage. Of course if it does leak and gets into enclosure its an excuse to replace panel. FEMA, National Manufacturers Association, IAEI, all recognize this as a hazard.That would seem to be a design choice, and not a safety issue.
True thatAt 7' AFF the PVC is not in the working space so that is not an issue. The issue is with the dedicated equipment space.
I agree that it is a violation. It just is not one that matters any.At 7' AFF the PVC is not in the working space so that is not an issue. The issue is with the dedicated equipment space.
I agree too given the setting but the pipe could leak into the panel.I agree that it is a violation. It just is not one that matters any.
True, but it would then require a drip pan or some other leak protection.The pipe could be 6 feet above the panel on a legal location and still leak.
I can't tell for sure from the picture but it looks to me like it is in front of the PB, not above it in the dedicated equipment space.True, but it would then require a drip pan or some other leak protection.
If so there is no violation.I can't tell for sure from the picture but it looks to me like it is in front of the PB, not above it in the dedicated equipment space.