NEC Subsection 110.3(C)
xptpcrewx
Power System Engineer
Las Vegas, Nevada, USA
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Per 110.3(C) Does all equipment have to be Listed? (in particular Power Circuit Breakers) Please provide supporting reason by code reference. Thanks in advance.
Yes. by a recognized qualified electrical testing laboratories
Equipment.
A general term, including fittings, devices, appliances, luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
110.1 Scope.
This article covers general requirements for the examination and approval, installation and use, access to and spaces about electrical conductors and equipment; enclosures intended for personnel entry; and tunnel installations.
110.3(C) Listing.
Product testing, evaluation, and listing (product certification) shall be performed by recognized qualified electrical testing laboratories and shall be in accordance with applicable product standards recognized as achieving equivalent and effective safety for equipment installed to comply with this Code.
Equipment.
110.1 Scope.
110.3(C) Listing.
Thanks. So any specific mention to using listed equipment; i.e. listed pressure connectors in other Articles of the code are merely redundant? (I understand 110.3(C) to be relatively new)
110.3(C) does not require anything to be listed. Read carefully what it actually says and not what you think it says.
Given that 110.3(C) is located under “Requirement for Electrical Installations”, what would be the purpose of 110.3(C) if not to require listing?
Read what it actually says. Carefully!!!
(C) Listing. Product testing, evaluation, and listing (product
Code.
This is solely a requirement for who can do the listing.
Code.
This is solely a requirement for who can do the listing, not that any product be listed.
I’ve read it carefully several times. I’m not concluding anything either way.
Im trying to understand why this would be for those doing the listing when the NEC is an installation standard.
If they did not define who could list something, you could list it.
Thanks. Any way to know how this got added in the first place and any reasoning behind it? I don’t see it in the first draft report of the 2017 edition or PC.
There are a few places in the Code where equipment is required to be LISTED. (680.24, Pool Lighting j boxes is an example)
All installations must be APPROVED, normally by the inspector/AHJ, and listing is one tool they can use.
you certainly made your point though I would like to know if you have per code installed fittings, devices, appliances, luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation that have not been listed.
It is done all the time. many things are not required to be listed by code. Some are. Some customers do not care. I can't even get some customers to farm out the extra few bucks to get their control panels UL listed.
Items that are required to be listed are specifically called out in article sections.
Roger