Art. 220 p. III. for special loads references other parts of the code (e.g. elevator). For general lighting, you would use table 220.12. So for corridors, halls and stairways you'd calculate 1/2 VA/Sq ft. For storage spaces you'd calculate 1/4 VA / Sq ft, etc. Electric space heaters would be 100% continuous. No VA requirement for "convenience receptacles " but would be for a receptacle serving a specific load, like a sump pump.I know how to calculate dwelling units demand factor but what about house loads for a house panel in apartment building? What VA/sq ft should I use per NEC table 220.12?
How can there be no requirement for VA/sq ft for receptacles? Could I use 1VA/sqft for receptacles if I wanted to? Is it a judgment call on what VA/sqft for receptacles is?Art. 220 p. III. for special loads references other parts of the code (e.g. elevator). For general lighting, you would use table 220.12. So for corridors, halls and stairways you'd calculate 1/2 VA/Sq ft. For storage spaces you'd calculate 1/4 VA / Sq ft, etc. Electric space heaters would be 100% continuous. No VA requirement for "convenience receptacles " but would be for a receptacle serving a specific load, like a sump pump.
Sent from my SM-A326U using Tapatalk
No. In residential, any receptacles that are not part of a special circuit, like the kitchen appliance circuits, laundry, bathroom GFI, are considered part of the general lighting circuits. So the VA/Sq ft applies to lighting and receptacles. You can have unlimited receptacles on these circuits. For lighting, you are limited by the maximum wattage rating ofbthe fixtures.How can there be no requirement for VA/sq ft for receptacles? Could I use 1VA/sqft for receptacles if I wanted to? Is it a judgment call on what VA/sqft for receptacles is?
Yea but but I’m talking about public light and power AKA house loads, not dwelling units.No. In residential, any receptacles that are not part of a special circuit, like the kitchen appliance circuits, laundry, bathroom GFI, are considered part of the general lighting circuits. So the VA/Sq ft applies to lighting and receptacles. You can have unlimited receptacles on these circuits. For lighting, you are limited by the maximum wattage rating ofbthe fixtures.
Bad advice I believe...public areas of an apartment complex do not fall under rules for the actual apartments themselves.No. In residential, any receptacles that are not part of a special circuit, like the kitchen appliance circuits, laundry, bathroom GFI, are considered part of the general lighting circuits. So the VA/Sq ft applies to lighting and receptacles. You can have unlimited receptacles on these circuits. For lighting, you are limited by the maximum wattage rating ofbthe fixtures.
Look over table 220.12 again.Yea but but I’m talking about public light and power AKA house loads, not dwelling units.
Also, do you count motors at 100% demand when doing house loads?
Right. That's why I advised looking at 220.12. There are specific VA/sq ft. rules for different areas.Bad advice I believe...public areas of an apartment complex do not fall under rules for the actual apartments themselves.
Can't use 220.84 because there are gas ranges. Also 220.14C is not clear because those articles mentioned don't tell you what demand to do. Are motors considered 100% demand?Look over table 220.12 again.
Mptors....see 220.14C, probably should be reading all of 220.14 a few times over.
Do your apartment loads allow you to use 220.84 ?
I am sorry, I struggled to follow.Right. That's why I advised looking at 220.12. There are specific VA/sq ft. rules for different areas.
220.84…you can use if it benefits you. I am very sure your gear size will fall.Can't use 220.84 because there are gas ranges. Also 220.14C is not clear because those articles mentioned don't tell you what demand to do. Are motors considered 100% demand?
If I do the exception, then all the apartment services will be too high which results larger wire and overcurrent protection because of adding the 8kw for range220.84…you can use if it benefits you. I am very sure your gear size will fall.
Read the exception that follows 220.84 A 2.
430.24 - follow 1-4. If you are looking for some multiplier that lets you reduce your total motor or hvac load by some percentage…it does not exist.
What does the first sentence of 220.84 say…If I do the exception, then all the apartment services will be too high which results larger wire and overcurrent protection because of adding the 8kw for range
I got to be the dumbest engineer out there lol! I can't believe I didn't realize this the key sentence...What does the first sentence of 220.84 say…
This is about sizing feeders to meter stacks and the overall service calc for the building.
What are you using for calculating these values ? 220 part 3 or part 4 ?
I believe you stated you had 140 apartments.
If you have a total apartment load calculated…let’s say 20kVa per unit x 140 = 2800kVA. Using table 220.84 let’s you knock that 2800 x .23 down to 644kVA.
Adding the 8kW per unit is just for the feeder and service calls to mimic them actually having an electric range which then gives you access to table 220.84.
Could you clarify what that condition actually means?I forgot to ask, but you must also meet criteria of 220.84 A 1…meaning ALL apartment loads are served by apartment panel. In all of these threadsI don’t believe you ever mentioned have systems or hot water.
In your example you didn’t add the 8kva range per unit, shouldn’t it be 28kva per unit not 20kva like you said, am I missing something?What does the first sentence of 220.84 say…
Everything powered within the apartment, the source must be the apartment panel.Could you clarify what that condition actually means?
Hot water is supplied by the building panel.Everything powered within the apartment, the source must be the apartment panel.
The 20kVA number was just a number…assumed the range load was already added in.
It was just to show you the value of gaining access to table 220.84.