220v20A gfci

Status
Not open for further replies.

sparky23

Member
Location
texas
so today we replaced zinsko panel with new - and there is a 20A single pole. 2 screws (so 220v) gfci breaker - what in a residence is 20A 220v? or required to be gfci 20A protected 220v?

thanks in advance - no one else to ask
 
It could be a spa heater or a spa, swimming pool, car charger etc. I assume it was installed before the 2020 so those are a few things it could be. Maybe bath floor heat although most of those have gfci in the t-stat but the ec may not have known that.
 
we didnt chase just replaced - so it got a new 220v 20Agfci double pole ch breaker
i just had no one to ask what it could be - no space or floor heater no spa,
 
I'm not aware of Zinsco ever producing a 2 pole GFCI breaker. Can't find anything online, have to dig out an old catalog and see. If it has 2 screws it's a 120v GFCI, line and neutral. 3 screws if it's a 2 pole GFCI. I'm guessing you just sent 240v to some bathroom and or outside receptacle circuit.
 
I'm not aware of Zinsco ever producing a 2 pole GFCI breaker. Can't find anything online, have to dig out an old catalog and see. If it has 2 screws it's a 120v GFCI, line and neutral. 3 screws if it's a 2 pole GFCI. I'm guessing you just sent 240v to some bathroom and or outside receptacle circuit.
I’m thinking someone needs to make a return trip to that job. On their own dollar and quickly.

eta: And label the panel properly while there.
 
If you look closely you will see that the white wire on the right side is a neutral and the black wire is the hot. The neutral line side is connected to the neutral bar but the circuit load side neutral is connected to the breaker.
 
That's a single pole GFCI breaker. If it was a 2-pole there would be another terminal for the neutral. Should have looked at the old GFCI, it would say whether it is 120V or 240V, but you should be able to determine that from the wiring. Looks like someone just yanked wires out without seeing what/how they were landed.

First thing I do on a panel change is find all the white wires on the breakers or fuses, then mark them to identify them as hot/ungrounded conductors. Then check for MWBC and tape them together and mark the neutral for them. Also check for any color besides white or green on the neutral bar. If I find another color, I tape it white or green to identify it as either an EGC or neutral.
 