How did you correctly label the circuits?we didnt chase just replaced - so it got a new 220v 20Agfci double pole ch breaker
i just had no one to ask what it could be - no space or floor heater no spa,
I’m thinking someone needs to make a return trip to that job. On their own dollar and quickly.I'm not aware of Zinsco ever producing a 2 pole GFCI breaker. Can't find anything online, have to dig out an old catalog and see. If it has 2 screws it's a 120v GFCI, line and neutral. 3 screws if it's a 2 pole GFCI. I'm guessing you just sent 240v to some bathroom and or outside receptacle circuit.
Sure looks like a load neutral next to the hot, is that a screw terminal above the line neutral?i have a picture - it is a 2 hot nuts with one toggle and the pigtail
I agreeIt looks like a 1p GFCI breaker to me.
That is what it is, for a really rare breed, try to find a Zinsco/Sylvania GFCI breaker in a bolt-on model, only have seen one once, the plug-in was fairly common in it's heyday.It looks like a 1p GFCI breaker to me.