NathanVA
- Alexandria, VA
- Master Electrician and Electrical Contractor
Ever been toe to toe with an inspector when he's dead wrong? He or she holds the cards, of course... and to paraphrase the Comedian Lewis Black "If you're standing in line and you need help from someone, you can't say 'Listen here, a-hole, you're an idiot!!' ... you have to tone that down".... I love me some Lewis Black. Anyway, I digress. Diplomacy and polite discourse are really the only way to win friends and influence people. But it sure isn't easy
Case in point: Outdoor Nema 14-50 Receptacle at a residence. We're using 2017 NEC. I failed an inspection because the receptacle does not have GFCI protection.
He's applying 210.8(B) - Other than dwelling units. When I point out that we should be using (A) since it's a dwelling unit. He retorts "well, we're outdoors, so we're not exactly *in* a dwelling unit"....
I have to count in my head to 10 so I don't explode. I take a breath and politely remind him to take a look at 210.8(A)(3) - Dwelling units, outdoors.
He said he's spoken with several supervisors and it's their consensus that 210.8(B) applies... but he was willing to speak with a county engineer for their interpretation and get back to me tomorrow.
Fingers crossed?
I'm sure you all have had similar experiences. Anyone else care to share their war stories? Any advice on pushing back against a misinterpretation?
Fingers crossed?