120volt control circuits for a motor starter and floats in a sump pump. Do white conductors need to be “phased” with tape a different color?
No single conductors.Is this in a cable?
No a white single conductor can not be reidentified. Just pull in a bulk, red, etc color
4 and larger blk can be reidentified as white or gray
I don't know of a rule that the base color has to be black, but there is a rule that you can't re-identify a white.When conductors do get re-identified thru tape, other than when they start as part of a manufactured cable, is there any rule requiring black wire to be the "blank canvas"?
But white can only be used for ungrounded
What about when we use NM for a switch leg?White can only be used for grounded. Or, white cannot be used for ungrounded.
I'm sure that's what you meant, just correcting for the record.
The colors of wires in manufactured cables are always permitted to be reidentified how ever you see fit.What about when we use NM for a switch leg?