Alwayslearningelec
 - NJ
 - Estimator
Its only overkill if you assume the service and voltage regulation are ideal. 80% load is typical for load flow analysis, but without any context its hard to say.This seems like overkill. VD usually want to keep under 3% and why 80% of the OCPD?
makes complete sense. But then this same engineer has a 400A breaker feeding a 400A panel 600' away with (1) 4" PVC & 4#600's which is wrongThe feeder for a building is usually permanent whereas the tenants or occupants in a building change. Your voltage drop should ideally take into account future loads.
For example, if you were doing a shell retail building there wouldn’t be any loads initially but then when a tenant moves in the load would be added to which would increase the voltage drop. You would want to make sure the feeder is sized for the future load so 80% would likely be a fairly accurate but conservative estimate.
The 80% isn’t a code requirement, it’s good practice.
Thank so basically your saying if I have 400A breaker feeding 400A panel @ 480v attached VD calculator would be the input parameters.The 80% is to allow for possible future expansion otherwise you could just use the calculated load which would be the present load.
Let's say that you 800 feeder has a calculated load of 400 amps, if you use 400 amps in you VD calc then when adding a few hundred amps in the future the VD will increase. 80% is just providing a reasonable buffer for the future unknown.
what is wrong with it?makes complete sense. But then this same engineer has a 400A breaker feeding a 400A panel 600' away with (1) 4" PVC & 4#600's which is wrong
It’s unlikely #600s could feed a 400A panel 600 feet away. VD would probably be extreme.
Basically they want you to calculate with a load of 80% of the feeder size and use conductors large enough to get down to 2% or less VD. For a 1000 amp feeder you would use 800 amps in your calculation.Thank so basically your saying if I have 400A breaker feeding 400A panel @ 480v attached VD calculator would be the input parameters.
So when the calculator says enter current at end of run it would be 80% of OCPD as I did?
Right but engineer note said VD to be under 2%.Actually if it’s 480 then it’s probably fine. I get about 3.4% VD fully loaded.
I don't 100% follow.Basically they want you to calculate with a load of 80% of the feeder size and use conductors large enough to get down to 2% or less VD. For a 1000 amp feeder you would use 800 amps in your calculation.
400*80%=320 ampsI don't 100% follow.. Soto check the feeder sizes already given by the engineer and comply with his note what would you input( or would of he) for a 400A breaker feeding a 400A panel at 480v.?
No I understand that. For the VD calculation the calculator said to put the current at the end of the cable run which would be the 80% of the OCPD... so not the load??400*80%=320 amps
Yes they told you specifically to use 80% not the calculated load.No I understand that. For the VD calculation the calculator said to put the current at the end of the cable run which would be the 80% of the OCPD... so not the load??
Yes, we're talking about calculating voltage drop which requires that you input into the VD formula the amount of current that will be on the feeder. For a 400 amp feeder they're telling you to use (400*80%) =320 amps when you input the current into the VD calculator. Does that make sense? Why don't you give us all of the numbers (length, voltage, feeder ampacity, Cu or Al) and we can run some examples.OK Guess I’m a little lost. If you take 80% of the overcurrent protection device that will result in smaller wire Being needed.
400A breaker feeding a 400A MCB panel 600' away. The feeder they have designed is a (1) 4" conduit w/ 4#600 THHN.Yes, we're talking about calculating voltage drop which requires that you input into the VD formula the amount of current that will be on the feeder. For a 400 amp feeder they're telling you to use (400*80%) =320 amps when you input the current into the VD calculator. Does that make sense? Why don't you give us all of the numbers (length, voltage, feeder ampacity, Cu or Al) and we can run some examples.
1. My point is if your designing with future expansion in mind( good practice but I guess pricey) wouldn't you want to oversize the wire a bit?
2. When designing and electrical system, simple scenario for feeding a panel that will feed loads the steps in my mind, in correct order would be!!??
A. Calculate totals loads panel will feed.
B. Size panel accordingly.
C. Size OCPD that will feed panel according to panel rating.
D. Size wire according to OCPD size.