xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
This seems like overkill. VD usually want to keep under 3% and why 80% of the OCPD?
Its only overkill if you assume the service and voltage regulation are ideal. 80% load is typical for load flow analysis, but without any context its hard to say.
 

Npstewart

Senior Member
The feeder for a building is usually permanent whereas the tenants or occupants in a building change. Your voltage drop should ideally take into account future loads.

For example, if you were doing a shell retail building there wouldn’t be any loads initially but then when a tenant moves in the load would be added to which would increase the voltage drop. You would want to make sure the feeder is sized for the future load so 80% would likely be a fairly accurate but conservative estimate.

The 80% isn’t a code requirement, it’s good practice.


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The 80% is to allow for possible future expansion otherwise you could just use the calculated load which would be the present load.

Let's say that you 800 feeder has a calculated load of 400 amps, if you use 400 amps in you VD calc then when adding a few hundred amps in the future the VD will increase. 80% is just providing a reasonable buffer for the future unknown.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
The feeder for a building is usually permanent whereas the tenants or occupants in a building change. Your voltage drop should ideally take into account future loads.

For example, if you were doing a shell retail building there wouldn’t be any loads initially but then when a tenant moves in the load would be added to which would increase the voltage drop. You would want to make sure the feeder is sized for the future load so 80% would likely be a fairly accurate but conservative estimate.

The 80% isn’t a code requirement, it’s good practice.


Sent from my iPhone using Tapatalk
makes complete sense. But then this same engineer has a 400A breaker feeding a 400A panel 600' away with (1) 4" PVC & 4#600's which is wrong
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
The 80% is to allow for possible future expansion otherwise you could just use the calculated load which would be the present load.

Let's say that you 800 feeder has a calculated load of 400 amps, if you use 400 amps in you VD calc then when adding a few hundred amps in the future the VD will increase. 80% is just providing a reasonable buffer for the future unknown.
Thank so basically your saying if I have 400A breaker feeding 400A panel @ 480v attached VD calculator would be the input parameters.
So when the calculator says enter current at end of run it would be 80% of OCPD as I did?
 

Attachments

  • Capture.JPG
    Capture.JPG
    98.2 KB · Views: 6

Npstewart

Senior Member
It’s unlikely #600s could feed a 400A panel 600 feet away. VD would probably be extreme.


Sent from my iPhone using Tapatalk

Actually if it’s 480 then it’s probably fine. I get about 3.4% VD fully loaded.


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank so basically your saying if I have 400A breaker feeding 400A panel @ 480v attached VD calculator would be the input parameters.
So when the calculator says enter current at end of run it would be 80% of OCPD as I did?
Basically they want you to calculate with a load of 80% of the feeder size and use conductors large enough to get down to 2% or less VD. For a 1000 amp feeder you would use 800 amps in your calculation.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Basically they want you to calculate with a load of 80% of the feeder size and use conductors large enough to get down to 2% or less VD. For a 1000 amp feeder you would use 800 amps in your calculation.
I don't 100% follow. 😩. Soto check the feeder sizes already given by the engineer and comply with his note what would you input( or would of he) for a 400A breaker feeding a 400A panel at 480v.?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No I understand that. For the VD calculation the calculator said to put the current at the end of the cable run which would be the 80% of the OCPD... so not the load??
Yes they told you specifically to use 80% not the calculated load.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
OK Guess I’m a little lost. If you take 80% of the overcurrent protection device that will result in smaller wire Being needed.

So in my scenario above you would need two sets of 400 MCM?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
OK Guess I’m a little lost. If you take 80% of the overcurrent protection device that will result in smaller wire Being needed.
Yes, we're talking about calculating voltage drop which requires that you input into the VD formula the amount of current that will be on the feeder. For a 400 amp feeder they're telling you to use (400*80%) =320 amps when you input the current into the VD calculator. Does that make sense? Why don't you give us all of the numbers (length, voltage, feeder ampacity, Cu or Al) and we can run some examples.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Yes, we're talking about calculating voltage drop which requires that you input into the VD formula the amount of current that will be on the feeder. For a 400 amp feeder they're telling you to use (400*80%) =320 amps when you input the current into the VD calculator. Does that make sense? Why don't you give us all of the numbers (length, voltage, feeder ampacity, Cu or Al) and we can run some examples.
400A breaker feeding a 400A MCB panel 600' away. The feeder they have designed is a (1) 4" conduit w/ 4#600 THHN.

1. My point is if your designing with future expansion in mind( good practice but I guess pricey) wouldn't you want to oversize the wire a bit?

2. When designing and electrical system, simple scenario for feeding a panel that will feed loads the steps in my mind, in correct order would be!!??
A. Calculate totals loads panel will feed.
B. Size panel accordingly.
C. Size OCPD that will feed panel according to panel rating.
D. Size wire according to OCPD size.
 

Npstewart

Senior Member
400A breaker feeding a 400A MCB panel 600' away. The feeder they have designed is a (1) 4" conduit w/ 4#600 THHN.

1. My point is if your designing with future expansion in mind( good practice but I guess pricey) wouldn't you want to oversize the wire a bit?

2. When designing and electrical system, simple scenario for feeding a panel that will feed loads the steps in my mind, in correct order would be!!??
A. Calculate totals loads panel will feed.
B. Size panel accordingly.
C. Size OCPD that will feed panel according to panel rating.
D. Size wire according to OCPD size.

1) Yes over sizing the feeders for the future possible loads is the responsible way to design. The expense is minimal and the probability of the panel being used to its capacity is fairly probable.

2) Yes, those are correct steps but they are starting points only. You need to make sure those steps match your specific situation, like when you have a 600 foot run. I personally would have requested an additional utility transformer because a 600 foot feeder isn’t really the ideal case.


Sent from my iPhone using Tapatalk
 