I came across this in a text book and before I contact the author I want to throw it out here and see if you agree. I totally disagree. It seems like he is trying to say that multiwire branch circuit grounded conductors must be grouped but if the isn't a multiwire branch circuit then it doesn't need it as shown in "G". I think he is overlooking 200.4
Here is the explanation for fig G
200.4 Neutral Conductors. Neutral conductors shall be installed
in accordance with 200.4(A) and (B).
(A) Installation. Neutral conductors shall not be used for
more than one branch circuit, for more than one multiwire
branch circuit, or for more than one set of ungrounded feeder
conductors unless specifically permitted elsewhere in this Code.
(B) Multiple Circuits. Where more than one neutral conductor
associated with different circuits is in an enclosure, grounded
circuit conductors of each circuit shall be identified or
grouped to correspond with the ungrounded circuit conductor(
s) by wire markers, cable ties, or similar means in at least
one location within the enclosure.