I came up with 305 Amps for the optional method.Did not include the neutral calc or the largest motor.
Feeder:
111.8 standard
73.8 optional
29280 VA
Service:
458 standard
322 optional
175680 VA
2 sets of 4 / 0 THWN Cu in separate conduits
For 3 phase:
Feeder:
125.0 standard
85.2 optional
29280 VA
Service:
339 standard
214.7 optional
175680 VA