LT Sparky
- Farwell, TX, United States
- Estimator Project Manager
I have a 10" deep 12 meter stack. Can I put a 12" deep gutter underneath it? It will be sticking out 2" further than the meter stack enclosure.
			Ok, I'll take one for the team and get things started:
I agree.I don't see why not.
Thats the thread that got me thinking it possibly could be a problem.We recently had a discussion about a pair of panels that were only 1/8" different in depth.
There were mentions of using strut or washers to match front surfaces of different depths.
Does being side-by-side vs being above-and-below really make that much of a difference?
Thanks that helps.110.26 (A)(3) allows other "associated equipment" to extend up to 6" beyond the front. I've seent hat rule used many times in regard to gutters/wireways.
Does whether it's beside the equipment matter as opposed to above and/or below?110.26 (A)(3) allows other "associated equipment" to extend up to 6" beyond the front. I've seent hat rule used many times in regard to gutters/wireways.
I'm going to through a wrench into this. The allowance is specifically uses "associated equipment". A raceway is not equipment based on the artical 100 definition.
Equipment. A general term, including fittings, devices, appliances, luminaries, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
if you look at definition of a raceway it never uses the term "equipment" .
In my opinion you need to find a different article to support that installation other than 110.26.
This requirement allows the placement of a 12 inch × 12 inch wireway on the wall directly above or below a 6-inch-deep panelboard without encroaching on the working space. The requirement prohibits large differences in depth of equipment below or above other equipment that specifically requires working space. Freestanding, dry-type transformers are not permitted to be installed where they extend into the work space for a wall-mounted panelboard. This compromises clear access to the panelboard.
Write a code proposal to include raceways and enclosures into the language of the allowance in 110.26. Then enforceable, otherwise a gung ho EI will jam you up for it because of a strict reading of that section. Common practice doesn't make compliance.I know this isn't "code enforceable" but this is the commentary for 110.26(A)(3) from the 2017 handbook:
Key word as to "the like" what is the reference referring back to? All the items proceeding the "and the like". Are any of those any type of raceway or enclosure?"and the like used as a part of, or in connection with, an electrical installation."
Has to be above or below.Does whether it's beside the equipment matter as opposed to above and/or below?
I'll disagree, on the basis that apparatus is not an NEC defined term, and it can easily be read to include raceways.I'm going to through a wrench into this. The allowance is specifically uses "associated equipment". A raceway is not equipment based on the artical 100 definition.
Definition of gutter and it's use is listed in Article 366. According to 366.2 an auxiliary gutter is an enclosure used to supplement wiring spaces at meter centers, distribution centers, switchgear, switchboards, and similar points of wiring systems.Is a gutter a raceway?
By definition it would appear a gutter is NOT a raceway but rather an enclosure.Definition of gutter and it's use is listed in Article 366. According to 366.2 an auxiliary gutter is an enclosure used to supplement wiring spaces at meter centers, distribution centers, switchgear, switchboards, and similar points of wiring systems.
Think it falls into all gutters are raceways but not all raceways are gutters.
A wireway is a raceway in accordance with the definition of raceway in Article 100. Auxiliary gutters supplement enclosure wiring spaces and are not encompassed by the definition of raceway. Therefore, NEC® requirements that apply only to raceways do not apply to auxiliary gutters. An example of such a requirement is 230.7, which prohibits service conductors from being installed in a raceway with conductors that are not service conductors. This rule applies to wireways installed in accordance with Articles 376 and 378. However, an auxiliary gutter installed to supplement the wiring space of a service equipment enclosure is not a wireway and, therefore, is not subject to 230.7.