Fordean
- New Jersey
- Electrical Contractor
Installing a power washer. Service is 120/208y
Need to install a transformer to boost to 480amp 3ph @48amp. We were talking about a 50kVA. But this is 10 weeks out.
So we are going with a 75kva and just running 1/0 with no neutral from Service to Trans. Then # 6 thhn to power washer outside 130 feet away.
I intend to fuse the line side 120/208v @ 150amp and load 480 @ 60amp.
Was just think. Does a motor starter need to be use with overload? Never seen such a large portable. Wundering if I forgot the motor protection if required. Not sure if something is on unit. Cord comes with tinned ends. Intend to use a 60 amp 600volt 3ph cord end. 4wire without neutral.. I dont see a 3 wire cord end. I dont require a neutral.