We are installing a 800 Amp SER ATS between the POCO Transformer and existing MDP, we were going to intercept those feeds in a trough around to new ATS then back to MDP.
The trough will be mounted under MDP to intercept 2 - 4" PVC C with 4 - 500 MCM each which we will use inline Polaris or compression lugs to extend to ATS, inspector says there is not enough room to bring conductors into trough because we will not comply with bending radius which my understanding is there is nothing in NEC to deal with bending radius on anything less than 600 volt and this is 277/480 Volt system.
The trough will start under panel and carry on around the wall to the ATS location then another trough above the other one back to MDP. I have 18" from floor to bottom of MDP to fit a trough, MDP is 12" deep. We were planning to use a 16" x 16" trough which has 51.2 usable SQ IN.
The trough will be mounted under MDP to intercept 2 - 4" PVC C with 4 - 500 MCM each which we will use inline Polaris or compression lugs to extend to ATS, inspector says there is not enough room to bring conductors into trough because we will not comply with bending radius which my understanding is there is nothing in NEC to deal with bending radius on anything less than 600 volt and this is 277/480 Volt system.