Mustwin351
- Texas
I came across the following installation: An air compressor with two 480v 3 phase motors 7.5 hp, nameplate 9 amps with each motor having a motor starter on the wall fed from a single branch circuit fused at 30 amps.
I wanted to check that ground fault and short circuit rating was sized correctly but was having a hard time finding in the code how to exactly size the individual branch circuit.
Do you add the motors together (11 amps each per 430.250) and multiply by 1.75 for time delay fuses?
430.53(B) states If the branch circuit short circuit and ground fault protective device is selected not to exceed that allowed by 430.52 for the smallest rated motor, two or more motors, or one or more motors and other loads with each motor having individual overload protection shall be permitted to be connected to a branch circuit where it can be determined that the branch circuit short circuit and ground fault protective device will not open on the most severe normal conditions of service that might be encountered.
Any thoughts?
Any thoughts?