Might make some difference I guess. What I was talking about at was from 2017.What year are you on ?
I agree. I was thinking 08 may have had some room descriptions. Also like you said the ceiling ones were not required. But we just put them everywhere even in detached garages.Might make some difference I guess. What I was talking about at was from 2017.
Since TR was introduced many just put them everywhere as there normally isn't many permitted to not be TR.
Looking at 2008, it just mentions areas covered by 210.52. No exceptions in that edition. Technically a receptacle over 5.5 above floor is not a 210.52 outlet and shouldn't been required to be TR anyway.I agree. I was thinking 08 may have had some room descriptions. Also like you said the ceiling ones were not required. But we just put them everywhere even in detached garages.
I think you answered the OP's question with that.Looking at 2008, it just mentions areas covered by 210.52. No exceptions in that edition. Technically a receptacle over 5.5 above floor is not a 210.52 outlet and shouldn't been required to be TR anyway.
Gotta catch me first.Keep in mind if you replace a receptacle in a location that is required to be TR,WR, GFCI or AFCI, the replacement is required to TR,WR, GFCI or AFCI
Menards is still selling non TR plugmold.My local habitat for humanity resell store has boxes of non TR receptacles. Not saying I have bought any..,,
What year are you on ?
At a continuing ed class about 5 years ago inspector quoted that TR receptacles in homes were not needed for receptacles over 7' off floor so appears only ceiling mounted garage door opener receptacles and maybe some wall clock receptacles would be exempt. Have not seen a clock receptacle installed in about 40 years. My sparky dad installed one in our house back in the late 50's and I got to help. Yep held the flashlight during the day time. My 96 year mom still has a clock plugged into my first helper job.see 406.12.
Basically all receptacles covered by 210.52 need to beTR receptacles.
exception says if over 5.5 feet above floor - seems redundant to have that exception though as one over 5.5feet isn't covered by 210.52 anyway.
7 feet maybe a local amendment.?At a continuing ed class about 5 years ago inspector quoted that TR receptacles in homes were not needed for receptacles over 7' off floor so appears only ceiling mounted garage door opener receptacles and maybe some wall clock receptacles would be exempt. Have not seen a clock receptacle installed in about 40 years. My sparky dad installed one in our house back in the late 50's and I got to help. Yep held the flashlight during the day time. My 96 year mom still has a clock plugged into my first helper job.
Generally no. Only going to be maybe 3 to 5 total you can omit in many homes. Especially it if you can't trust your employees to remember to get them in the right spot and an inspector ends up catching it.Not worth the effort to omit any TRs in a residence. IMO.
2011 NECWhat year are you on ?
Okay, that's the year as Ramsy said. The NEC made TR's required when swapping an existing outlet. 406.4 (D) 52011 NEC
Not worth the effort to omit any TRs in a residence. IMO.