luke_
Member
- Location
- Washington
- Occupation
- Commercial Electrical Maintenance
Hello, i’m doing a 320 amp overhead service for my personal home. I do mostly commercial so I do not have a great handle on residential services. I have done a 320 service before but they’ve all been underground. My situation is the following: I’m coming over head to a customer owed pole with a 320 meter can mounted on the pole. From the 320 meter can I will be going to two 200 amp disconnects. From one of the disconnects I will go straight to the house. The other disconnect will go to a 200 amp ATS and then from the ATS to the house. The ATS I have does not have a service disconnect so I need to have a disconnect in front of it. I will be using 4/0 2/0 aluminum with a ground to go from the 200 amp disconnects to the house. Neither panel will have a load rating greater than 180 Amps. The biggest question I have is the size of the conductors that go up the mast. Looking at the NEC service conductor size I believe 500mcm Aluminum would be adequate. some things may seem odd but with my materials but I’ve had to improvise a little Because of product shortages. I also have a question on the ground I will be running a ground from one disconnect through the two ground rods and back up to the other disconnect. Will number 4 copper be acceptable for this Since I’m going to each disconnect? or do I need to size it to the 500mcm? Which would be 1/0.
thanks for the help.
thanks for the help.