steve holt
- Hawaii
Do outlets located within a base cabinet count towards the number required for wall spacing?  I could have sworn the NEC said they do not, but I cant find anything.
			So if the outlet is located in the wall behind the cabinet, and the cabinet is cut out to access the outlet it is leagal because its within 18" of the wall?See 210.52(3)
210.53(3) says that receptacle outlets in cabinets are not part of the required wall receptacle outlets.So if the outlet is located in the wall behind the cabinet, and the cabinet is cut out to access the outlet it is leagal because its within 18" of the wall?
I take it you mean built-in, not free-standing, which begs more questions:This came up years ago and a few of the code panel members stated that a room with nothing in it but bookshelves would not require a receptacle since there was no wall space.
Is there a requirement to not block existing receptacles with free-standing bookcases?
Must existing receptacles either be made accessible or the circuit abandoned if you build-in bookcases?
Ok now I see it.210.53(3) says that receptacle outlets in cabinets are not part of the required wall receptacle outlets.
There is no requirement for a minimum distance to a sink. The receptacle can be directly over the sink but certainly a bad placement IMO.I learned something. question, is there a requirement for receptacle spacing around a sink? and if so would that override the receptacle spacing requirement? What is the minimum spacing from a sink with a gfci and without? i'm thinking a utility sink in a garage.
IMO a built in bookcase doesn't block a required receptacle.WA has a rule if a bookcase for example, blocks a required receptacle, then an additional receptacle must be added elsewhere
In addition to what Dennis said there is no spacing requirements in a garage plus in a garage all receptacles would require GFCI protection anyway.I learned something. question, is there a requirement for receptacle spacing around a sink? and if so would that override the receptacle spacing requirement? What is the minimum spacing from a sink with a gfci and without? i'm thinking a utility sink in a garage.
My father stacked ordinary bookshelves and secured them to the living room wall on one side. He cut out the back of the bookshelves anywhere they wound up in front of a receptacle. Problem solved. Nothing says you can't put a book in front of a receptacle.IMO a built in bookcase doesn't block a required receptacle.
If a room has nothing but book case and doorways on all the walls I think is possible there is no "required" receptacles in that room.
Floor receptacles? You put them within 18" of what? There is no wall requiring any receptacles. Any receptacles in said room are in addition of minimum required which is zero.
I'm sure this shakes many inspector's heads though.
I agree.My father stacked ordinary bookshelves and secured them to the living room wall on one side. He cut out the back of the bookshelves anywhere they wound up in front of a receptacle. Problem solved. Nothing says you can't put a book in front of a receptacle.
is a gfci required for a 240v receptacle?In addition to what Dennis said there is no spacing requirements in a garage plus in a garage all receptacles would require GFCI protection anyway.
If you are on 2020 NEC, yes.is a gfci required for a 240v receptacle?
the one in my garages isn't!!! i don't think it would be possible as current could be equal on both legs or some could be returning on neutral.