marmathsen
- Seattle, Washington ...ish
- Electrical Contractor
So we've been have a running commentary between myself and one of my guys.
NEC 2020 210.52(A)(2)(1) requires receptacles outlets to be placed in any wall space that is 2 ft or more that is unbroken by a "fixed cabinets that [does] not have countertops". Implying that you are still required to install one if said cabinet does have a countertop.
Furthermore, both 210.52(A)(4) and 210.52(C) state that any receptacle installed for coutertops "shall not be considered as the receptacle outlets required by 210.52(A)"
Am I missing something? Doesn't this all explicitly say that in the kitchen of a dwelling that you are required to not only install countertop receptacles per 210.52(C) but also wall receptacles per 210.52(A). Where do the 210.52(A) receptacles go? In the toe kick? Does anyone actually do that?!
Someone please tell me what I'm missing.
210.52(A)(2) Wall Space.
As used in this section, a wall space shall include the following:
- (1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets that do not have countertops or similar work surfaces
210.52(C) Countertops and Work Surfaces.
In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop and work surfaces that are 300 mm (12 in.) or wider shall be installed in accordance with 210.52(C)(1)through (C)(3) and shall not be considered as the receptacle outlets required by 210.52(A).