From 2017 NEC:
location.
ARTICLE 518
Assembly Occupancies
518.1 Scope. Except for the assembly occupancies explicitly
covered by 520.1, this article covers all buildings or portions of
buildings or structures designed or intended for the gathering
together of 100 or more persons for such purposes as deliberation,
worship, entertainment, eating, drinking, amusement,
awaiting transportation, or similar purposes.
518.2 General Classification.
(A) Examples. Assembly occupancies shall include, but not be
limited to, the following:
Armories Exhibition halls
Assembly halls Gymnasiums
Auditoriums Mortuary chapels
Bowling lanes Multipurpose rooms
Club rooms Museums
Conference rooms Places of awaiting transportation
Courtrooms Places of religious worship
Dance halls Pool rooms
Dining and drinking Restaurants
facilities Skating rinks
(B) Multiple Occupancies. Where an assembly occupancy
forms a portion of a building containing other occupancies,
Article 518 applies only to that portion of the building considered
an assembly occupancy. Occupancy of any room or space
for assembly purposes by less than 100 persons in a building of
other occupancy, and incidental to such other occupancy, shall
be classified as part of the other occupancy and subject to the
provisions applicable thereto.
So is the place of worship a stand alone building/Structure or is is it part of a multiple occupancy Building. Like a Place of Worship in a strip mall.
I would think that alone would guide you to the answer.
2017 NEC:
518.4 Wiring Methods.
(A) General. The fixed wiring methods shall be metal raceways,
flexible metal raceways, nonmetallic raceways encased in
not less than 50 mm (2 in.) of concrete, Type MI, MC, or
AC cable. The wiring method shall itself qualify as an equipment
grounding conductor according to 250.118 or shall
contain an insulated equipment grounding conductor sized in
accordance with Table 250.122.
Usually there is a plaque require at the entrance of a building defining the occupancy limits. No plaque call the city or Fire Marshall. If under 100 and a stand alone building and no amendments I would say you're OK. Last note; Watch out for an historical district location.
One item to help would be look at existing wiring methods. No need to scab it up