Morning! An engineer designed a project we are doing (2 of them) with a 750 Aluminum secondary run instead of parallel runs. We didnt have time to wait for an RFI answer as the slab was being poured and were told to "install per plan". We now have 1 ea 4" PVC in the slab for this 750 Aluminum run. The issue is now with the power company. They cannot terminate 750 in their transformer and 750 will not fit in the meter base. (we cant get the meter for 8 months anyway due to the crisis we are all facing with electrical gear lol) Can we use the tap rule in 240.21 and reduce the wire size that will fit in the lug? I checked on the pin reducers and these will not reduce the 750 down small enough.
Been a while since I was on the forum. Good to be back on!
Thanks all.