Kopper
- Lewisburg, Pennsylvania, USA
- Electrical Contractor
This is the situation:
We installed a 50A Generator inlet (Reliance PBN-50) using 6/3 Romex to a 50A breaker in the panel box with a Generator interlock installed. We supplied the homeowner with a 50A cord with a NEMA 14-50P on one end and a CS6365 on the other to plug into the inlet. The homeowner has a generator with a NEMA6-15R which he wants to use to provide power to run a couple things during a power outage. I found an adapter that goes from NEMA 6-15P to NEMA 14-50R that will allow him to connect the generator to the house.
Problem:
What about neutral since there is no neutral on a NEMA 6-15 configuration?
Problem: