hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have dwelling unit bathroom where heated floor mat is provided. Its Suntouch Tapat amp drawn at 240V single phase is 1A per 20 sf, watf density is 12W/sq ft.
The bathroom is 7.67ft x 12.17 ft so that 93.31 sq ft.
The total watts is 1116 watts at 240V single phase so the total amps comes to 4.67A.
I was wondering what would be the breaker size in panelboard be 20A or 15A? Plans show 20A with #12 awg cable
The bathroom is 7.67ft x 12.17 ft so that 93.31 sq ft.
The total watts is 1116 watts at 240V single phase so the total amps comes to 4.67A.
I was wondering what would be the breaker size in panelboard be 20A or 15A? Plans show 20A with #12 awg cable
floor sensing thermostat. (Listed separately) Voltage: 120 VAC, 240 VAC, 1-phase (see Table 2) Watts: D12 and C12 Series - 12 W/ft2 (41 Btu/h/ft2 ), C15 Series 15 W/ft2 (51 Btu/h/ft2 ) Maximum circuit load: 15 A Maximum circuit overload protection: 20 A breaker GFCI: (Ground Fault Circuit Interrupter) required for each circuit (included in the SunStat control)