I have dwelling unit bathroom where heated floor mat is provided. Its Suntouch Tapat amp drawn at 240V single phase is 1A per 20 sf, watf density is 12W/sq ft.

The bathroom is 7.67ft x 12.17 ft so that 93.31 sq ft.

The total watts is 1116 watts at 240V single phase so the total amps comes to 4.67A.

I was wondering what would be the breaker size in panelboard be 20A or 15A? Plans show 20A with #12 awg cable
 
New word for you: "Google"
Specifications for TapeMat: Floor heating mats are a simple way to heat an indoor space. This instruction manual is provided as a guide to installing TapeMats, including design considerations, installation steps, limitations, precautions, and floor covering guidelines. TapeMat is a complete heating mat consisting of a series heating wire and a power lead for connection to the electric power supply. The heating wire length cannot be cut to fit. Controls: TapeMats must be controlled by a SunStat® floor sensing thermostat. (Listed separately) Voltage: 120 VAC, 240 VAC, 1-phase (see Table 2) Watts: D12 and C12 Series - 12 W/ft2 (41 Btu/h/ft2 ), C15 Series 15 W/ft2 (51 Btu/h/ft2 ) Maximum circuit load: 15 A Maximum circuit overload protection: 20 A breaker GFCI: (Ground Fault Circuit Interrupter) required for each circuit (included in the SunStat control)
 
New word for you: "Google"
Specifications for TapeMat: Floor heating mats are a simple way to heat an indoor space. This instruction manual is provided as a guide to installing TapeMats, including design considerations, installation steps, limitations, precautions, and floor covering guidelines. TapeMat is a complete heating mat consisting of a series heating wire and a power lead for connection to the electric power supply. The heating wire length cannot be cut to fit. Controls: TapeMats must be controlled by a SunStat floor sensing thermostat. (Listed separately) Voltage: 120 VAC, 240 VAC, 1-phase (see Table 2) Watts: D12 and C12 Series - 12 W/ft2 (41 Btu/h/ft2 ), C15 Series 15 W/ft2 (51 Btu/h/ft2 ) Maximum circuit load: 15 A Maximum circuit overload protection: 20 A breaker GFCI: (Ground Fault Circuit Interrupter) required for each circuit (included in the SunStat control)

Not exactly what i have from engineer. Doesnt say recommended breaker size?

1313959fb4b86fab298de0a509492be5.jpg



Sent from my iPhone using Tapatalk
 
Chances are your drawings say "field verify". So your actual usage is 4.6 ams with an additional continuous load brings you to 6 amps or under. A 15A circuit on 14AWG is plenty
 