I have dwelling unit bathroom where heated floor mat is provided. Its Suntouch Tapat amp drawn at 240V single phase is 1A per 20 sf, watf density is 12W/sq ft.
The bathroom is 7.67ft x 12.17 ft so that 93.31 sq ft.
The total watts is 1116 watts at 240V single phase so the total amps comes to 4.67A.
I was wondering what would be the breaker size in panelboard be 20A or 15A? Plans show 20A with #12 awg cable
The bathroom is 7.67ft x 12.17 ft so that 93.31 sq ft.
The total watts is 1116 watts at 240V single phase so the total amps comes to 4.67A.
I was wondering what would be the breaker size in panelboard be 20A or 15A? Plans show 20A with #12 awg cable