readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
Readout on generator shows a little over 62hz, is this anything to worry about?

Its 10kw, manual switching for some circuits, including refrig, freezer, air conditioner, lights

volts 241
 
Your motors will turn a little faster, but it's no cause for alarm. Tight frequency control is only required when there's more than one generator connected to the same grid. Synchronous clock motors, some digital clocks (that use line frequency for their time reference), and some of the clocks embedded in electronic gadgets will run fast and need to be reset.
 
What are you reading frequency with, analog or digital meter?
I've never checked frequency with meter, this was display on (cheap) generator, can scroll through volts, hz, hours runtime

Customer furnished generator so its not my problem if there is a problem but sounds like no problem
 
Usually it will drop under load.
I agree, might even run just shy of 60 if well loaded or be all over the place (within some tolerance band) when load is not steady. Smaller the "flywheel" the harder it is to maintain a steady frequency when load changes, which is a part of reason why utility frequency is very stable compared to smaller sources.
 